Azure managed disk LRS redundancy

Assaf L 261 Reputation points
2023-01-22T08:41:52.16+00:00

According to the documentation, LRS disks are replicated 3 times within a single data center (details).

At the 18/1 there was a single zone power event with this sentence explaining what went wrong (taken from Azure status history site):

While all server racks have redundant dual feeds, one feed was powered down for maintenance, and a failure in the redundant feed caused a complete shutdown of the affected racks.

The sentence above describes replication process of 2 times (dual feeds)

Can you explain the difference between the documentation and the incident?

Azure Disk Storage
Azure Disk Storage
A high-performance, durable block storage designed to be used with Azure Virtual Machines and Azure VMware Solution.
573 questions
{count} votes

Accepted answer
  1. SaiKishor-MSFT 17,201 Reputation points
    2023-01-31T23:16:25.5333333+00:00

    @Assaf L Adding more information to the above-

    These are referring to two different things. #1, LRS disks have data replicated 3 times (across 3 different racks). #2, Racks have dual power supply. If both the feeds supplying to a rack go down, the rack goes out of power. In the 1/18 incident, multiple (more than 2) racks lost power due to both power supplies down.

    Does that answer your question? Please let me know. Thanks!

    Remember:

    Please accept an answer if correct. Original posters help the community find answers faster by identifying the correct answer. Here is how.

    Want a reminder to come back and check responses? Here is how to subscribe to a notification.

    1 person found this answer helpful.

1 additional answer

Sort by: Most helpful
  1. Luke Murray 10,526 Reputation points MVP
    2023-01-23T00:47:00.2266667+00:00

    Hi, Assaf

    This doesn't indicate storage replication, this refers to electrical components required for running the gear:

    The electrical feeds are dual, but during maintenance, when it was running on 1 out of the 2 - the 2nd one failed.

    This unexpected event was caused by a failure in the electrical systems feeding the affected racks. While all server racks have redundant dual feeds, one feed was powered down for maintenance, and a failure in the redundant feed caused a complete shutdown of the affected racks. We continue to investigate the nature of this redundant feed failure to prevent incident reoccurrence.